Was a there a code requirement for an individual branch circuit for a kitchen hood? I havent had to do residential/houses in a while, and I do remember times in the past we would run a seperate circuit for the kitchen hood in case it got changed over to a microwave/hood combo, and I believed it was code required. Now I cannot locate it in the NEC.
 

Buck Parrish

Senior Member
Location
NC & IN
Was a there a code requirement for an individual branch circuit for a kitchen hood? I havent had to do residential/houses in a while, and I do remember times in the past we would run a seperate circuit for the kitchen hood in case it got changed over to a microwave/hood combo, and I believed it was code required. Now I cannot locate it in the NEC.
A dedicated circuit is / was not requiredired for the regular hard wired hood. 422.16 (Unless required by the instructions)
 

tortuga

Code Historian
Location
Oregon
Occupation
Electrical Design
If the hood fan motor is over 6 amps 430.53 will apply. Other than that you wont find anything.
 