6 618electrician Member Location St. Louis Occupation Maintenance electrician Yesterday at 6:29 PM #1 how many and where and where not . 2017 nec ?????????????????????????????????????????????????????????????????????????????????????????
how many and where and where not . 2017 nec ?????????????????????????????????????????????????????????????????????????????????????????
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician (retired) Yesterday at 6:50 PM #2 2017 one receptacle required. Typcially put on one of the ends.
R rc/retired Senior Member Location Bellvue, Colorado Occupation Master Electrician/Inspector retired Yesterday at 6:51 PM #3 At least one. Not more than 12" below the countertop. Face up in the countertop. 210.52(C) for dwellings. None for commercial kitchen islands that I can find. Ron
At least one. Not more than 12" below the countertop. Face up in the countertop. 210.52(C) for dwellings. None for commercial kitchen islands that I can find. Ron