J jim123 Member Location new castle,de Sep 12, 2018 #1 The new freezer needs a 3 pole single phase receptical. It needs a 14-20 recep.2017 code 220.8 B states u need a gfci protection.(Which will be a breaker.). Will the gfci trip on this application
The new freezer needs a 3 pole single phase receptical. It needs a 14-20 recep.2017 code 220.8 B states u need a gfci protection.(Which will be a breaker.). Will the gfci trip on this application
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Sep 12, 2018 #2 It will work just fine with a 2 pole GFCI circuit breaker.