Kitchen light trips pool pump

Status
Not open for further replies.

brantmacga

Señor Member
Location
Georgia
Occupation
Former Child
Had a weird one yesterday guys.

Sent a guy to a house on the market to make repairs from a HI report. Turning on the fluorescent kitchen light switch tripped the GFCI in the main feeding the pool panel.

I went out and opened the panel cover; kitchen light circuit breaker is directly across from the 30/2 ITE GFI breaker, and it falls off the bus. I replaced the 20/1 breaker and the problem went away.

Customer calls this morning and said it happened again. I went back out, moved the 20/1 circuit lower on the panelboard to get it away from the GFCI, still trips.

I replaced the 30/2 GFI with a standard breaker, and added a GFCI for the pump in the pool panel (the lighting circuit in the pool panel had its own GFI breaker). Problem went away again. I stayed for awhile toggling the switch repeatedly and it never came back.

Also, I visually traced the 10/4 tray cable from the main panel to the pool panel to make sure nothing was tapped off it.

30/2 was the only GFI in the panel; I chalked it up to the combination of an old magnetic ballast and an old GFI breaker, beyond that any other thoughts?


Sent from my iPhone using Tapatalk
 
It would have been neat if you had left the old GFCI breaker and rebuilt the light with a T8 ballast and then seen what happened. I do know from experience GFCI's don't always like T12 ballasts on their load side but I hadn't ever seen a T12 affect a gfci on a whole different circuit.

I agree that AFCI's do all kinds of crazy stuff. I once seen a new fancy treadmill that was leaking 0.1 amps of current on a ground prong trip every AFCI in the panel when the customer tried to use it. Another time at my house I only half flipped my bedroom light switch in a sleepy daze and so it started arcing a little inside the switch. That caused the built in AFCI in a small portable space heater on an entirely different circuit to pop.
 
Old GFCI breaker that is subject to line side faults/fluctuations in power? Maybe rated (or not) for reverse feed so line side problems are seen as load side? I assume the pool circuit neutral is to the breaker and pigtail is to the buss?

Did you try a newer GFI breaker, or straight delete it for GFCI receptacle at the pump?
 
....I hadn't ever seen a T12 affect a gfci on a whole different circuit.

I haven't either.

However, I've posted numerous times about my experience at a big box pet store having a modern T8 instant start ballast trip seven different circuit GFCI breakers that were in the same panel as the dedicated circuit that fed the display with the ballast. I replaced the Advance ballast with a different brand and the nuisance tripping ceased.
 
Old GFCI breaker that is subject to line side faults/fluctuations in power? Maybe rated (or not) for reverse feed so line side problems are seen as load side? I assume the pool circuit neutral is to the breaker and pigtail is to the buss?

Did you try a newer GFI breaker, or straight delete it for GFCI receptacle at the pump?

I installed a new QO GFI breaker at the pool panel.


Sent from my iPad using Tapatalk
 