Had a weird one yesterday guys.
Sent a guy to a house on the market to make repairs from a HI report. Turning on the fluorescent kitchen light switch tripped the GFCI in the main feeding the pool panel.
I went out and opened the panel cover; kitchen light circuit breaker is directly across from the 30/2 ITE GFI breaker, and it falls off the bus. I replaced the 20/1 breaker and the problem went away.
Customer calls this morning and said it happened again. I went back out, moved the 20/1 circuit lower on the panelboard to get it away from the GFCI, still trips.
I replaced the 30/2 GFI with a standard breaker, and added a GFCI for the pump in the pool panel (the lighting circuit in the pool panel had its own GFI breaker). Problem went away again. I stayed for awhile toggling the switch repeatedly and it never came back.
Also, I visually traced the 10/4 tray cable from the main panel to the pool panel to make sure nothing was tapped off it.
30/2 was the only GFI in the panel; I chalked it up to the combination of an old magnetic ballast and an old GFI breaker, beyond that any other thoughts?
Sent from my iPhone using Tapatalk
Sent a guy to a house on the market to make repairs from a HI report. Turning on the fluorescent kitchen light switch tripped the GFCI in the main feeding the pool panel.
I went out and opened the panel cover; kitchen light circuit breaker is directly across from the 30/2 ITE GFI breaker, and it falls off the bus. I replaced the 20/1 breaker and the problem went away.
Customer calls this morning and said it happened again. I went back out, moved the 20/1 circuit lower on the panelboard to get it away from the GFCI, still trips.
I replaced the 30/2 GFI with a standard breaker, and added a GFCI for the pump in the pool panel (the lighting circuit in the pool panel had its own GFI breaker). Problem went away again. I stayed for awhile toggling the switch repeatedly and it never came back.
Also, I visually traced the 10/4 tray cable from the main panel to the pool panel to make sure nothing was tapped off it.
30/2 was the only GFI in the panel; I chalked it up to the combination of an old magnetic ballast and an old GFI breaker, beyond that any other thoughts?