Kitchen Receptacles

Status
Not open for further replies.

Siboney

New member
What is the minimum number and spacing of receptacles in a residential kitchen? Do they all have to be GFCI or AFCI?

Thanks
 
Take a look at 210.11(C)(1), 210.52(A),(B), & (C) and for the GFCI requirements see 210.8(A)(6), there is no requirement for AFCI protection of a kitchen in the 2005 NEC.

Chris
 
I am closing this thread, in accordance with the Forum?s rules. This Forum is intended to assist professional electricians, inspectors, engineers, and other members of the electrical industry in the performance of their job-related tasks. However, if you are not an electrician or an electrical contractor, then we are not permitted to help you perform your own electrical installation work.

If I have mis-judged this situation, if for example you are designing a residential building, then send me a Private Message, and I will reopen the thread.
 