do recepticals NOT serving countertops or appliances in kitchens have to be 20 amp GFCI or can they be 15 amp GFCI
marinesgt0411 said:do recepticals NOT serving countertops or appliances in kitchens have to be 20 amp GFCI or can they be 15 amp GFCI
All in kitchen yes.Dining room is a maybemarinesgt0411 said:do recepticals NOT serving countertops or appliances in kitchens have to be 20 amp GFCI or can they be 15 amp GFCI
marinesgt0411 said:do recepticals NOT serving countertops or appliances in kitchens have to be 20 amp GFCI or can they be 15 amp GFCI
If they are not serving the counter tops:
- no, they don't need to be GFI protected. 210.8(A)(6)
- no, they don't need to be 20A
What he is referring to is the actual receptacle itself. The device isn't required to be 20A. (Table 210.21(B)(2))infinity said:No receptacles in a dwelling are required to be 20 amps.
What he is referring to is 210.52(B)(1) exception 1.Jim Walker said:All in kitchen yes. Dining room is a maybe