Is there a listed knob and tube connector for bringing knob and tube into a panel board?
Is there a listed knob and tube connector for bringing knob and tube into a panel board?
Is there a listed knob and tube connector for bringing knob and tube into a panel board?
Is that NM cable sheath?To connect to a panel you will have to sleeve the conductor in order to go to less than a three inch separation. . . what about this?
![]()
Is that NM cable sheath?
If so that is creative, don't know how easily it would be approved by an inspector.
I'm sincerely asking.Article 394
Concealed Knob-and-Tube Wiring
394.19 Clearances.
(A) General. A clearance of not less than 75 mm (3 in.) shall be maintained between conductors and a clearance of not less than 25 mm (1 in.) between the conductor and the surface over which it passes.
(B) Limited Conductor Space. Where space is too limited to provide these minimum clearances, such as at meters, panelboards, outlets, and switch points, the individual conductors shall be enclosed in flexible nonmetallic tubing, which shall be continuous in length between the last support and the enclosure or terminal point.
To connect to a panel you will have to sleeve the conductor in order to go to less than a three inch separation. . . what about this?
![]()
Is that NM cable sheath?
If so that is creative, don't know how easily it would be approved by an inspector.
However one does it, you need to bring all conductors of a circuit through same hole in a ferrous enclosure or cut slots between the holes so you effectively only have one hole to minimize inductive effects.
I agree that the assembly in the photo above is quite interesting. There is a lot of understanding going on in the assembly, in my opinion.
I'm pretty sure that it is NM cable sheath. Let's say that, in fact, it is. . . what is "un-approvable", by NEC rule, about it?
I'm sincerely asking.
I've just crawled through the White Book and the NFPA Glossary, and, of course, the NEC, and I'm finding, I believe, that "flexible nonmetallic tubing" is undefined.
Both if you call it heat shrink tubing:happyyes:I have used both heat shrink and clear plastic tubing.
Both of which are non metallic and flexible, and the word "tubing" is in one of them!![]()
Is there a listed knob and tube connector for bringing knob and tube into a panel board?
In my experience, "loom" is, in fact "flexible nonmetallic tubing" as used in NEC Article 394.I have heard before that "flexible nonmetallic tubing" in the context of 394 refers to loom-I have no proof that that is the true definition, just what was heard.
The sheath on NM-B is definitely evaluated (by NRTLs) for the mechanical protection of the insulated conductors within the sheath, it is non-conductive, and it is flexible. One can quibble over whether 12/2 sheath is exactly cylindrical, and whether "fibrous" is required.IEEE 100
The Authoritative Dictionary of IEEE Standards Terms
Seventh Edition
flexible nonmetallic tubing (loom) A mechanical protection for electric conductors that consists of a flexible cylindrical tube having a smooth interior and a single or double wall of non-conducting fibrous material. See also: raceway.[/b]
I also find it interesting that putting "wire loom" or "flexible nonmetallic tubing" into a search engine brings a LOT of results.
A lot of the search engine returns are commonly aimed at the automotive industry, but there is obviously a lot of application for all manner of use with all manner of wiring. . . just saying.
Personally, I've always managed to have a stock of early 1900s "fibrous" loom that has satisfied my needs in the field. I will find old specimens of loom in wiring demo and save the good flexible lengths for reuse.
Until I bumped into the assembly in the photo above in this thread, I had never really given thought to how I would handle running out of my small stock of historic loom. I believe that the use of NM sheath is a really smart use of a contemporary product for an historic wiring method mechanical protection.
Google "braided wire loom" or / and look at Cable Ties and More's page.I couldn't find any with a smooth interior,
Google "braided wire loom" or / and look at Cable Ties and More's page.
Given the synthetic cloth we wear in various ways as clothing, nylon, rayon, polyester, etc., a woven plastic fiber, I think that the term "fibrous" is satisfied.
I believe that is a verbal hall-of-mirrors that one can be distracted by. . . smooth at a quantum level? smooth at a molecular level? How far to go. . .The stickler, if one was to be technical, is the 'smooth inside'.
I realize I haven't directly addressed your question. I, initially, couldn't think of a connector that I knew had a rating for "knob and tube".Is there a listed knob and tube connector for bringing knob and tube into a panel board?
I believe that is a verbal hall-of-mirrors that one can be distracted by. . . smooth at a quantum level? smooth at a molecular level? How far to go. . .
Well, if the insulated conductor can slide into the length of loom required for the physical protection needed to satisfy Article 394, isn't that adequately smooth? The looms we are looking at are definitely free if burrs and sharp cutting edges or other protrusions that would damage the conductor insulation, in my opinion.