Bubbles666 said:I know this is sacro-ligious but you twist it very gently about 4 inches on each side then solder very carefully then reslide loom back over. And put it on a 15 amp arc fault breaker. Oooo..it hurt to say that!
peter d said:Putting knob and tube on an arc-fault breaker would be quite useless as K&T does not contain a ground wire, and AFCI's are more effective at "finding" N-G faults and parallel arcs than series arcs.
TSET said:Mark, I'm getting "file damaged" or some such response whe I try to download either PDF. Could you send the files (not links) to my email??
That is: TRSTSE@Lanset.com
Much appreciated, Todd
TSET said:From what I could glean(sp) from the posts, it sounds like you can feed old K&T from new romex, but not the reverse?
I don't want to get into soldering (especially in a hot attic), so J-boxing is the way to go, but the flying neutral only, or hot only splices need re-work, containment, and jumpers. It seems, from my reading, that there is no allowed single conductor or Romex usage for thse jumpers. Its a rule for me never to use old wire in repairs, due to unknowns, so it seems there is no repair option, for some of this work, just replacement. Have I read this right?
augie47 said:Peter, I think the latest generation of arc-faults is effective at series faults also