brother
Senior Member
As a practice we usually put knob and tube #12 on 15 amp protection. In your area do they allow you to put # 12 knob and tube on 20 amp protection?
Did they leave .09 change?In real life most K&T had 30s. Sometimes a penny, but I have seen a dime.
Are the current ratings different between an all copper penny and one of the post 1982 zinc/copper-clad ones? (Probably)Sometimes a penny, but I have seen a dime.
I don't think the 'free air' tables were used for concealed knob and tube (as opposed to open wiring).Original K&T was protected in accordance with Table 310.17 as the conductors are separated and in open air....20 amp protection of 15 amp K&T was legal before the small conductor rule was added to the code a few decades ago.
If they're being used in an Edison-base fusebox, I don't think the difference is significant.Are the current ratings different between an all copper penny and one of the post 1982 zinc/copper-clad ones? (Probably)
That's a little disturbing. Oh, well, it's on the Internet now. (and on a credible site, at that)... just score the copper fuse collar on either side of the fuse and bend one side down across the point of the fuse, screw it back in,, and ...
View attachment 2564994
If they're being used in an Edison-base fusebox, I don't think the difference is significant.
I generally didn't worry about K&T other than tell the owners it was there. Once AFCI came about the guys would manage to get them on one. For this area, there were usually only two circuits and those were mostly lighting nowadays.Of all things to worry about with K&T, ampacity doesn't make my list. Putting 12awg K&T on regular 15A breakers strikes me as a 'false sense of security' kind of thing.
Yeah probably the best use of an AFCI / GFCI breaker is K&T.Once AFCI came about the guys would manage to get them on one.
When a full removal is out of the question for costs I have been hired to just remove all the exposed in the attic runs and basement/crawl.There is allot of it around here.
Yeah probably the best use of an AFCI / GFCI breaker is K&T.
One time I went to a service call for some non working lights.
Older bungalow house probably late teens early 1920's, the customer was a very chatty lady, and was telling me every last detail while my apprentice somehow went in the tiny attic.
After a while he was making muffled yet loud noises, and I finally here him say 'I found it'.
I poked my head up there to see bright orange glowing splice, like a old car cigarette lighter.
There was blackened blow in insulation all around it.
The attic had just been insulated by a weatherization grant.
And it was obvious whomever did the work stepped all over the K&T, straining the brittle 90 YO splices.
Some of us are old enough to have seen steel wire run down the center of an attic...Comparing the current carrying capabilities of a copper penny vs. a 1982 zinc/copper penny is disturbing also if you're serious about it.
My post was simply a response to those of us old enough to witness code violations of penny's, dimes, etc,, that were installed behind screw in fuses to bypass the overcurrent protection.
And,
Examples of code violations are posted here on a daily basis.
JAP>