DaveNEC 1999 ARTICLE 320 -- Open Wiring on Insulators
320-3. Uses Permitted
Open wiring on insulators shall be permitted on systems of 600 volts, nominal, or less, only for industrial or agricultural establishments, indoors or outdoors, in wet or dry locations, where subject to corrosive vapors, and for services.
Trying to follow..........NEC 2002
300.3 Conductors.
(A) Single Conductors. Single conductors specified in Table 310.13 shall only be installed where part of a recognized wiring method of Chapter 3.(B) Conductors of the Same Circuit. All conductors of the same circuit and, where used, the grounded conductor and all equipment grounding conductors and bonding conductors shall be contained within the same raceway, auxiliary gutter, cable tray, cablebus assembly, trench, cable, or cord, unless otherwise permitted in accordance with 300.3(B)(1) through (4).
300.3(b).What now prevents you from running two NM circuits to some loads and using the hot from one cable and the neutral from the other cable,
I would argue this, and ask if you might agree with a simple definition of circuit.Roger,
What about 300.3(B)(3)? This section acts as an exception to the main part of the rule in 300.3(B).
Don