jeff43222
Senior Member
- Location
- Minneapolis, Minnesota
I was called in the other day on a job where a home inspector flagged a bunch of K&T splices and said they needed to be in j-boxes. The wiring in question is in joist cavities in the unfinished basement of a single-family dwelling. The splices he flagged weren't the original ones with the cloth tape and soldered connections; he flagged the ones that have been obviously done relatively recently (in once case, a bright red wire nut was visible under the tape).
I'm wondering how to proceed with this, as I'm not entirely convinced the code requires j-boxes in this case (all the wiring in question is K&T, no new wires were mixed in). Since this wiring method is no longer legal to install, the code doesn't have an article to address it (394 only applies to concealed K&T). Also, 300.15 doesn't mention this wiring method as one that requires a j-box for a splice.
And if a box is required, 314.3 seems to say I can't use nonmetallic boxes. If I have to use metal boxes, do I then have to ground all of them per 314.4?
I'm wondering how to proceed with this, as I'm not entirely convinced the code requires j-boxes in this case (all the wiring in question is K&T, no new wires were mixed in). Since this wiring method is no longer legal to install, the code doesn't have an article to address it (394 only applies to concealed K&T). Also, 300.15 doesn't mention this wiring method as one that requires a j-box for a splice.