O.K. guys clear this up for me. I've read the code book and all the threads.

If going into a j-box and I dont use the last K.O. of a concentric or eccentric K.O. it is still o.k. to use conduit (emt) as E.G. as long as the voltage is not over 250 volts.

I think it is, but wanted to ask to positive on this subject.

Thanks guys for any reply.
 
kbrandt said:
O.K. guys clear this up for me. I've read the code book and all the threads.

If you've read all the threads, you are more patient than me. :grin:

Have you read the exception to 250.97...?
 
short answer: yes
Plus, Frizebeedog's reference will show you it's normally o.k. over 250 volts.
 