reed179
Member
- Location
- Mansfield, ohio
I'm hoping someone had the answer before I spend thousands on a new control board. I have a150k kohler generator that's been giving me temperature reading problems. The background to the problem begins: I was performing a coolant flush. The generator was ran for 2 hours with a cleaner, drained and ran a water flush. Once I began the second water flush the water temp gauge didn't work. I ohmed the wires, they are good. I changed the sending unit located in the thermostat housing, which sends its signal directly to the gauge. I've changed the gauge. The resistor on the back of the gauge checks good. The gauge is getting correct voltage when the generator is running. Voltage is going from the temp sending unit to both the low temp light and the gauge. The light works as when I didn't have the heater plugged in and the water was cold, the low temp light was on. I switched the leads on the sending unit, the one to the light and gauge. The light works from both portions of the sending unit. The gauge will not work.
So, new gauge, tried 2 new temp sending units, checked wires, checked voltage and ohms. I don't have schematics for the board but I'm almost convinced the a resistor in the board which one set of witts runs through had gone bad. Any suggestions?
So, new gauge, tried 2 new temp sending units, checked wires, checked voltage and ohms. I don't have schematics for the board but I'm almost convinced the a resistor in the board which one set of witts runs through had gone bad. Any suggestions?