Looking to see if anyone has any information on a Kohler generator we typically install Briggs and Stratton. The ATS is straight forward but have never seen this set up before the (LO and the ground is jumped together) would I remove this jumper and use LO as my neutral? IMG_1888.jpeg
 
If it's feeding a panel or other load where the neutral-ground bond is made, I would remove the jumper.

I'd be surprised if this is not addressed in the instructions.
 
Looking to see if anyone has any information on a Kohler generator we typically install Briggs and Stratton. The ATS is straight forward but have never seen this set up before the (LO and the ground is jumped together) would I remove this jumper and use LO as my neutral? View attachment 2569848
A lot of the manufacturers put that jumper in, when 99% of the residential installations require it to be removed. If I remember correctly, Briggs and Stratton has it too, it’s just not as obvious. Unless the transferswitch switches the neutral, that jumper is to be removed.
 