Here is an excerpt from an OSHA document on field made cord sets.
Roger
2. The cord set must meet all applicable requirements of Subpart K. For example, the assembly must be marked appropriately (1926.403(g)); boxes intended for use in a permanent installation may not be used (1926.403(b)(1)(i)); cords must be connected to devices and fittings so as to provide strain relief (1926.405(g)(2)(iv)); cords passing through holes in enclosures must be protected by bushings or fittings designed for the purpose (1926.405(g)(2)(v)- fittings designed to fasten cables to metal boxes are not acceptable); and no grounded conductor shall be attached to any terminal or lead so as to reverse designated polarity (1926.404(a)(2)).
Roger