Greetings,
My customer has asked me to calculate the size of generator needed to power equipment in remote location. I have a generator specialist who will actually make the final calculation based on the nature of the load and starting sequence and match it to a gen-set. My task is to get the required loads and details on to a spread sheet and forward it to the gen guy. I have reviewed my reference books as well as the internet including several post on this forum and am still not clear.
The system will be 120/208 WYE. Grounded neutral. They are hoping for apx. 75KVA gen set.
VxAx1.73/1000, amps came from NEC 430.250
Watrer pump @ 25HP 3ph 208V.=26.92KVA
Water pump @ 7.5HP 3ph 208V.=8.711KVA
Water pump @ 10 HP 3ph 208V.=11.0.8KVA
hyd pump @ 7.5 hp 3PH 208v=8.71KVA
1ph 120v=???
2 BATTERY CHARGERS@120 V 2.4 KVA= 4.8KVA
1 BATTERY CHARGER@ 120 V 1.2 KVA = 1.2 KVA
70 LED LIGHT FIXTURES @ 120 V 19 W= 1.33 KVA
The equipment list is not final, what I need to know if you would be so kind, is if my 3 phase calc is accurate, and on the 120V loads do I tally the KVA up and make one fat total or do I balance the loads between phases, take the sum of the highest leg x 1.73? Or take the sum of the highest leg and X 3?
Also the generator specialist will take into the calculation the start up currents.
Regards,
Dick Carlton
My customer has asked me to calculate the size of generator needed to power equipment in remote location. I have a generator specialist who will actually make the final calculation based on the nature of the load and starting sequence and match it to a gen-set. My task is to get the required loads and details on to a spread sheet and forward it to the gen guy. I have reviewed my reference books as well as the internet including several post on this forum and am still not clear.
The system will be 120/208 WYE. Grounded neutral. They are hoping for apx. 75KVA gen set.
VxAx1.73/1000, amps came from NEC 430.250
Watrer pump @ 25HP 3ph 208V.=26.92KVA
Water pump @ 7.5HP 3ph 208V.=8.711KVA
Water pump @ 10 HP 3ph 208V.=11.0.8KVA
hyd pump @ 7.5 hp 3PH 208v=8.71KVA
1ph 120v=???
2 BATTERY CHARGERS@120 V 2.4 KVA= 4.8KVA
1 BATTERY CHARGER@ 120 V 1.2 KVA = 1.2 KVA
70 LED LIGHT FIXTURES @ 120 V 19 W= 1.33 KVA
The equipment list is not final, what I need to know if you would be so kind, is if my 3 phase calc is accurate, and on the 120V loads do I tally the KVA up and make one fat total or do I balance the loads between phases, take the sum of the highest leg x 1.73? Or take the sum of the highest leg and X 3?
Also the generator specialist will take into the calculation the start up currents.
Regards,
Dick Carlton