KVA Calculation

Status
Not open for further replies.
You have the calculation correct but it looks like you've computed it incorrectly.

(0.513A * 3) = 2.052A

* 277V = 568.404VA == .568KVA

That only represents that single phase load.
 
You have the calculation correct but it looks like you've computed it incorrectly.

(0.513A * 3) = 2.052A

* 277V = 568.404VA == .568KVA

That only represents that single phase load.


You have the concept correct but it looks like you've computed it incorrectly.
(0.513A * 3) = 1.54A (0.513A * 4) = 2.052A * 277 = 0.568 kva.
 