A 75KVA transformer will give you 75KW into a 100% resistive load. It will take slightly more than 75KVA input power to do that, due to transformer losses. Now most loads aren't resistive; they have a complex impedance. We describe these loads as having resistive and reactive components, and they shift the phase angle of the current away from being in-phase with the voltage. When that happens, the amount of KW that can be supplied starts dropping.
There is a ton of information on the internet on how to work the so-called 'power triangle', using KW, KVA, KVAR, and PF. For an example, lets take a 0.8 power factor load. PF=KW/KVA. A 75KVA transformer supplying a 0.8 power factor load will only be able to deliver 0.8=KW/75 or 60KW.