080609-0946 EST
I have started some experiments on a device called GreenPlug. Very little information at this point.
My experiments yesterday were on a freezer. The freezer was warm meaning the compressor would run continuously during my experiment. My assumption is that under these conditions the mechanical load from the compressor will remain constant. May or may not be valid. The initial assumption is that at a fixed load the mechanical power will be constant. But in reality the slip for a given load will increase for a lower input voltage. I have no easy way to measure the motor RPM.
Since the GreenPlug is supposed to modulate the voltage to the load I need to know how this compressor responds to voltage variations.
I allowed the compressor to stablize for about 1/2 hour then made the following measurements. The instruments were --- Fluke RMS meter with Hall device current probe, Simpson 75 watt full scale wattmeter with a current transformer, a Fluke average reading meter for voltage, and a 7.5 A Powerstat for an adjustable voltage source.
The results were as follows:
Code:
080608-1200 Power, Voltage, and Current measurements to a freezer compressor.
Voltage Current Power VA Power Factor
Volts Amperes Watts
100.1 3.74 319 374 0.853
100.2 3.68 319 368 0.867
109.9 3.62 323 397 0.814
120.1 3.55 332 426 0.779
120.2 3.56 332 427 0.778
130.3 3.8 349 495 0.705
130.3 3.7 344 482 0.714
These were not run in this order.
If in fact the mechanical output power was constant, then the efficiency improved with lower voltage. I do not know if this is true or not but I doubt it.
Assuming this constant output power is correct, then maximum saving from running at 100 V instead of 130 is only about 30 W. Refrigeration systems do not normally ruin continuously.
As pointed out by somone in one of the other threads on this subject turning lights off will save vastly more energy. I can not find that thread right now.
With the above data I was ready to run the test with the GreenPlug device. Problem --- with that device in line this compressor could not get started. It tripped its thermal overload.
Later I will try the test again on a different motor.
.