Hello,
I have a 600 kW Caterpillar GenSet with a 600 kVA UPS system that carry the load until the Generator is spooled up and the load is transferred with an ATS.
The kVA and kW ratings is a bit confusing to me. Below are some calculations for you review. We are needing to add 250 amps of current to our system and I am trying to decide if our generator and UPS is capable of handling the load.
We are currently running at approximately 286 kW which is 344 kVA. This is 60% of the 600 kVA UPS capacity.
Here is what I've come up with.
kW = √3 x PF x I x V / 1000
kW = 1.73 x 0.8 x 250 x 480 / 1000
kW = 166.08
Now to covert that to kVA…
kVA = kW / PF
kVA = 166.08 / 0.8
kVA = 207.6
Adding 207.6 kVA to this UPS that is already running approximately 344 kVA, that equals 551 kVA. Will that be overloading the UPS and/or the GenSet?
Any thoughts would be appreciated!
I have a 600 kW Caterpillar GenSet with a 600 kVA UPS system that carry the load until the Generator is spooled up and the load is transferred with an ATS.
The kVA and kW ratings is a bit confusing to me. Below are some calculations for you review. We are needing to add 250 amps of current to our system and I am trying to decide if our generator and UPS is capable of handling the load.
We are currently running at approximately 286 kW which is 344 kVA. This is 60% of the 600 kVA UPS capacity.
Here is what I've come up with.
kW = √3 x PF x I x V / 1000
kW = 1.73 x 0.8 x 250 x 480 / 1000
kW = 166.08
Now to covert that to kVA…
kVA = kW / PF
kVA = 166.08 / 0.8
kVA = 207.6
Adding 207.6 kVA to this UPS that is already running approximately 344 kVA, that equals 551 kVA. Will that be overloading the UPS and/or the GenSet?
Any thoughts would be appreciated!