kw to btu chart
A electric nickel chrome heater element produces 3.4 BTU/Hour
The very efficient mechanical refrigeration compressor produces 8.533 BTU/Hour+/-
I had a 4 ton unit 10 SEER that pulled 28 amps. That's 28x240 = 6720 kva /4ton = 1.7 kva per ton
One ton of frig.=12000 BTU/hour
1 watt=8.533 BTU/hour compressor
4 tons x 12,000=48,000 BTU/hour
48,000/8.533=5,625 watts 1.4 kw per ton 1.75 kva per ton
5,625/240 volts=23 amps more efficient machine
If you include the SEER, then you can do it another way. SEER is defined as the heat transferred per unit of energy, that is in BTU/watthour.
P = AC load/SEER
For your 4 ton unit and SEER = 10,
P = (48,000 BTU/hour)/(10 BTU/watthour) = 4,800 watts,
then throwing in PF,
I = P/(VxPF) = 4800W/(240V x 0.8) = 25A 1.2 kw per ton or 1.5 kva per ton
This is comparable to the other result.