Re: kWh vs. Demand load
WOW! You guys are all over the place.
The kWh has nothing to do with anything except power over a period of time. During that period of time, the amount of power may fluctuate all over the place. The kWh total is only the amount of energy used during that time period.
If you wish to measure the total instantaneous demand and the meter has a wheel, you may use this method.
1. Look at the meter for a Kh (secondary watt-hour constant) number, this is the meter constant and indicates the energy used by the load for each revolution of the disk. If you are looking at a CT cabinet, someone will have marked a multiplier and is used to increase the Kh value for the CT ratio.
2. Count the revolutions of the disk for one minute, if you want a little more accuracy, use a little more time.
3. Multiply the number of revolutions in one minute by the Kh, and then by 60. Divide the resultant by 1000.
Example:
You are at a service that has a meter with a Kh of 3.6 and time the turns at 68 per minute.
(68)(3.6)(60) / 1000 = 14.688 kW
If this is a single phase service, the load in amperes is
14.688 / 0.24 = 61.2 amperes
This is just an instant in time and is of no use for any kind of load study.
In general, residential and small commercial meters do not have the ability to register the demand. Additionally, the pulses are every 15 seconds instead of 30 minutes for the demand meters.