lmchenry said:If I know the kwh per month usage on a particular business, can I determine the service size needed for the business?
lmchenry said:They are adding on to the business and I dont think the service is big enough. At peak month they used 3397 kwh.
The KWH is of no value in determining the size of the service. You can have a demand of 100 kw for 1 hr and 5 kw for the rest of the month. The service must be sized for the max demand. You need to calculate the load as if it were a new service. As recommended, get the existing load and use 220 of the NEC for the rules and calculations.lmchenry said:If I know the kwh per month usage on a particular business, can I determine the service size needed for the business?
So true. Ultimately you will need the load calculation.bob said:The KWH is of no value in determining the size of the service. You can have a demand of 100 kw for 1 hr and 5 kw for the rest of the month. The service must be sized for the max demand. You need to calculate the load as if it were a new service. As recommended, get the existing load and use 220 of the NEC for the rules and calculations.
jrannis said:I gotta agree. Look at all of your motor loads in horse power. Look at your HVAC load. Any other heaters or equipment?
Do a load calculation of the existing building and add the addition.
You are going to have to have it done for a plan review if you want a permit.
James@CHA said:Get the demand load from the utility.
KWH is just there units of measure for charging the customer, the KW value however will tell you what you need to know. Typically you also get peak demand values.