D.Rater

Member
My understanding is that you can't have them in conduit together.Why? What then is the best way to do this; h/o wants GFI's and l.v. lights on stairs and deck.I'm trying to not clutter the outside wall with pvc and I'd LIKE to locate the transformer on basement joist.
 

websparky

Senior Member
Location
Cleveland, Ohio
Re: L.V and line voltage in conduit

Start with 725.52 for the first answer.

I would suggest running the LV wire exposed on the underside of the deck. Of course, you would need the proper type of wire.
 

busman

Senior Member
Location
Northern Virginia
Occupation
Master Electrician / Electrical Engineer
Re: L.V and line voltage in conduit

Also please note that most LV transformers for outdoor lights are listed for OUTDOOR use only.

Mark
 

thinfool

Senior Member
Location
Kentucky
Re: L.V and line voltage in conduit

you can't have them in conduit together.

I think you will find that this is not true. In fact, it is done all the time under the following conditions:

The conductors must be insulated with the same class of insulation. In practice that means that 12v or 24v conductors must have thhn 600v insulation if they are installed in a conduit with a 120v receptacle circuit.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: L.V and line voltage in conduit

I think you will find that this is not true. In fact, it is done all the time under the following conditions:

The conductors must be insulated with the same class of insulation. In practice that means that 12v or 24v conductors must have thhn 600v insulation if they are installed in a conduit with a 120v receptacle circuit.
Many of the low voltage lighting systems have a listed Class 2 power supply, and if so, then 725.55(A) prohibits the placement of these conductors in a common raceway.
Don
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Re: L.V and line voltage in conduit

The conductors must be insulated with the same class of insulation. In practice that means that 12v or 24v conductors must have thhn 600v insulation if they are installed in a conduit with a 120v receptacle circuit.
Don is correct, if the low voltage conductors are classified as class 2 then they cannot go into a conduit with 120 volt power conductors regardless of their insulation rating. It is a common misconception that they can if the insulation values for all of the conductors are rated for the highest voltage then it is permissible. This is untrue since it would violate 725.55 as Don mentioned.
 