Christmas break project for our school district
I am under the impression:
- all new 240 volt receptacle circuits are to be 4-wire
- 3-wire receptacles previously installed are grandfathered in when attaching new equipment via 250.140 (exception) with several qualifiers:
1. the neutral is insulated or SE that lands at service main panel
2. the exception is limited to dryers, ranges, or ovens
Situation A) A new 240 volt circuit for a 3 hp table saw attached via cord and plug in a detached building with a 100 amp sub panel under NEC 2017.
Am I correct that the circuit must be 4-wire? Our maintenance personnel will be running the circuit. He wants to use a L6-30R to match the other outlets.
I contend he must use a 4-wire circuit.
Situation B). Same location. We also have a new 240 volt planer. He wants to adapt the cord to use a previously installed 3-wire L6-30R.
I contend the exception specifically states dryer, range oven; that a new 4-wire circuit must be run.

His argument is the 4-wire requirement is for residential dwellings, not shops; that receptacles for 240 volt equipment are routinely run on 3-wire or even 2-wire devices.
His plan is to run two 10awg thhn with the conduit as the ground.
Is this code compliant?
Is 4-wire for dwellings only?
How far off am I?
I am under the impression:
- all new 240 volt receptacle circuits are to be 4-wire
- 3-wire receptacles previously installed are grandfathered in when attaching new equipment via 250.140 (exception) with several qualifiers:
1. the neutral is insulated or SE that lands at service main panel
2. the exception is limited to dryers, ranges, or ovens
Situation A) A new 240 volt circuit for a 3 hp table saw attached via cord and plug in a detached building with a 100 amp sub panel under NEC 2017.
Am I correct that the circuit must be 4-wire? Our maintenance personnel will be running the circuit. He wants to use a L6-30R to match the other outlets.
I contend he must use a 4-wire circuit.
Situation B). Same location. We also have a new 240 volt planer. He wants to adapt the cord to use a previously installed 3-wire L6-30R.
I contend the exception specifically states dryer, range oven; that a new 4-wire circuit must be run.

His argument is the 4-wire requirement is for residential dwellings, not shops; that receptacles for 240 volt equipment are routinely run on 3-wire or even 2-wire devices.
His plan is to run two 10awg thhn with the conduit as the ground.
Is this code compliant?
Is 4-wire for dwellings only?
How far off am I?