In the plant, 2 of our L6-30R receptacles on one panel show "NO GND" or "FLOATING GND". The receptacles all have good ground connection to the panel and to EARTH GND. The panel is supplied by a 480VAC 3Phase to a 240VAC 3Phase DELTA transformer with no center taps. All installed long before my time. Other than these 2 on this panel, all others in the plant show good grounds, not floating, no problems.
Should these be on a Wye transformer? Some equipment is 3 phase.
Or go thru a single phase 240 to 240/120 transformer?
Or is there something else that should be looked at?
Most equipment does run on these, but none that references GND.
Thanks,
Art
Should these be on a Wye transformer? Some equipment is 3 phase.
Or go thru a single phase 240 to 240/120 transformer?
Or is there something else that should be looked at?
Most equipment does run on these, but none that references GND.