We have an lab installation where we installed GFCI breakers to serve the receptacles along the countertops in the labs. Upon move-in, the Owner has experienced instantly tripping of the GFCI breaker when they start a device (ex. centrifuge). To troubleshoot, we verified the contractor had connected the neutrals correctly, both in the panel and at the receptacles. There are multiple (up to three single phase circuits) in a single conduit, but all have independent neutrals. The equipment did the same thing on any circuit we checked. We then tested the same piece of equipment on a GFCI receptacle and the equipment functioned properly. The breakers are Square D QOBs and we did verify the devices are correctly connected and also do not violate any of the installation instructions that could cause nuisance tripping (ex. <250 feet of load conductor, etc.). All lab spaces have individual panelboards, so distance should not be an issue. Has anyone experienced a similar incident or have suggestions?