The engineer supplied 2 calculations for afci.
The following data was obtained from ABC ELECTRIC on their 50KVA transformer:
a. Fault Current at the secondary of the 50KVA transformer = 19,768Amps.
ABC Engineering: calculated the Short-Circuit Fault Current at Panel "P".:
b. Calculated Fault Current at Panel “P” = 17,395Amps.
The Point to Point Method of Short-Circuit calculations was used to performed the
Fault Current Study calculation s at Panel "P"
Do both calculation go on service equipment? one on meter other on disconnect? or just disconnect? The service is an exisiting 6 gang meter bank. Our service is the last to be installed and will have the label. I am not sure where the label is going.
The following data was obtained from ABC ELECTRIC on their 50KVA transformer:
a. Fault Current at the secondary of the 50KVA transformer = 19,768Amps.
ABC Engineering: calculated the Short-Circuit Fault Current at Panel "P".:
b. Calculated Fault Current at Panel “P” = 17,395Amps.
The Point to Point Method of Short-Circuit calculations was used to performed the
Fault Current Study calculation s at Panel "P"
Do both calculation go on service equipment? one on meter other on disconnect? or just disconnect? The service is an exisiting 6 gang meter bank. Our service is the last to be installed and will have the label. I am not sure where the label is going.