Labeling requirements for low voltage power

Status
Not open for further replies.

lbridgeford

New member
I have a (hopefully) simple question. I have 24V powered VAV controllers that we are supplying power for via a 120>24V transformer with 5 output circuits (with breakers). What are the labeling requirements for the circuits if any exist? Does NFPA70 article 110.22 on labeling disconnects apply if these transformer breakers are the last point of isolation for a given number of controllers?

Thanks!
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
I have a (hopefully) simple question. I have 24V powered VAV controllers that we are supplying power for via a 120>24V transformer with 5 output circuits (with breakers). What are the labeling requirements for the circuits if any exist? Does NFPA70 article 110.22 on labeling disconnects apply if these transformer breakers are the last point of isolation for a given number of controllers?

Thanks!

take a look at 725.3
 