Labeling/Tagging

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
No but it might help the next guy if he has to troubleshoot something. Multiple neutrals in raceways may have additional requirements.
 

Elect117

Senior Member
Location
California
Occupation
Engineer E.E. P.E.
You are looking at 210.5 but there is nothing unless they are different voltage classes.

I have seen where it was tagged by breaker location where splices exist but never where circuits where just pulled through.
 

Seven-Delta-FortyOne

Goin’ Down In Flames........
Location
Humboldt
Occupation
EC and GC
Circuits, no.

But grounded conductors, high legs, and conductors of different voltages usually need to be identified where they are accessible.

There’s a lot of things that get specs that are not necessarily a Code requirement, but it’s just the way the owners want it done.

Im bidding one right now where 20 amp circuits are limited to 60’ length from the breaker. If it’s what they want it’s what they get. It just costs more.
 

Elect117

Senior Member
Location
California
Occupation
Engineer E.E. P.E.
Don't multiple neutrals in the same raceway need to be identified even when there is only one system say 208Y/120?

Ya, I was commenting on phase conductors.

And I never really thought of it as a requirement for neutrals where you are just pulling through because of the exceptions. I should probably pay more attention to it with splices.
 
Top