I have run EMT in metal framed buildings where the installed studs have pre-cut holes for running pipe and also can be twisted in order to facilitate installation. I've never tried doing that with wood studs except for single pieces here and there. I don't know the exact numbers, I can only guess based on experience:
If your EMT runs will all be vertical from the device boxes into ceiling space and then horizontal to interconnect, that will be very labor intensive.
If your EMT runs will be horizontal though the studs, that will be super labor intensive. I'm not even sure why anyone would want to. I would bid it at no less that 10 times normal EMT installation labor and be prepared to buy five times as many couplings.
MC cable or FMC would be much, much, much less expensive. I'm not a fan of Smurf tube, but that is another valid choice.