Lack of grounding-bonding near DP on a condo

Status
Not open for further replies.

Tomco

Member
Hello everyone, this thread is related to the condo where I live. I experience very bad lightning surges, lost a number of equipment already (three sets of cable company's setbox and modem, twotelevisions, one gaming console, one blu-ray player and one multi-channel AVreceiver) within 1,5 years and I suspect that it is related to grounding and bonding issues. I use a surge protector, and after a thorough investigation and analysis of the lost electronics, I was able to successfully trace the problem back to the coaxial cables. I let the cable company know about it, they claimed they meet NEC-requirements. However, I suspect they do not. Did quite a research in the NEC and according to that, I would have to say that at least the cables at the the Demarc Point need to be grounded with a ground block and electrode or rod, and bonded back to the main ground .

My questions:

  • Does the installation shown on the pictures meet NEC-requirements?
  • If not, what else needs to be added and done to the installation to meet requirements?

Apparently, I will not fix this myself, considering the facts that the cables belong to the cable company and I assume I cannot make modifications on them, but this represents a safety hazard in my home and I want someone to put an end to this.

I also do not know who to contact if the cable company won't be willing to fix the issue here if they are breaking the NEC.

Thank you!

Ps.: Sorry about the word "pipe" in the pictures, I meant conduit! And I also can provide pictures of the attic if needed, but the cables just simply enter.
 

Attachments

  • 1.jpg
    1.jpg
    96.4 KB · Views: 1
  • 2.jpg
    2.jpg
    139 KB · Views: 1
  • 3.jpg
    3.jpg
    125.1 KB · Views: 1
  • 4.jpg
    4.jpg
    129.1 KB · Views: 1
  • 5.jpg
    5.jpg
    95.4 KB · Views: 1
  • 6.jpg
    6.jpg
    83.8 KB · Views: 1
  • 7.jpg
    7.jpg
    89.9 KB · Views: 1

JFletcher

Senior Member
Location
Williamsburg, VA
Welcome. Your demarc is the box down low, not the one up high. Code requires the coax be bonded at the demarc; this is usually done via a green #14 run from the first splitter back to the panel. What you have looks correct tho what I need to see is not pictured (a bare or green wire coming from the first splitter/barrel connector to the service).

Grounding coax will not stop surges. You need a surge protector for coax, and that is no guarantee to stop surges either.

Interestingly enough, 30+ years ago when this neighborhood was cabled, the cable co. drove a 5' rod at the demarc, hooked a 3' piece of #14 from it to the first splitter, and called it a day. Never seen the first fried electrical component from this. Bonding the cable to the service is a bad idea imo but I'll never get the code changed so whatev..

btw, in pic #7, the cables touching the metal conduit arent an issue. If that was taking a lightning surge I'd expect to see scorch marks.
 

Tomco

Member
Welcome. Your demarc is the box down low, not the one up high. Code requires the coax be bonded at the demarc; this is usually done via a green #14 run from the first splitter back to the panel. What you have looks correct tho what I need to see is not pictured (a bare or green wire coming from the first splitter/barrel connector to the service).

Grounding coax will not stop surges. You need a surge protector for coax, and that is no guarantee to stop surges either.

Interestingly enough, 30+ years ago when this neighborhood was cabled, the cable co. drove a 5' rod at the demarc, hooked a 3' piece of #14 from it to the first splitter, and called it a day. Never seen the first fried electrical component from this. Bonding the cable to the service is a bad idea imo but I'll never get the code changed so whatev..

btw, in pic #7, the cables touching the metal conduit arent an issue. If that was taking a lightning surge I'd expect to see scorch marks.

Thank you so much for the fast response, JFletcher!

Seems like I will have a bunch of additional questions. You said the demarc is the cable box down below, for some reason I thought that that is the Network Interface Device (NID).

I relied on NEC Article 820 that says "the metallic sheath of CATV cable entering a building or structure must be grounded to the earth as close as practicable to the point of entrance to the building or structure" [820.33]. And the Demarcation Point (or point of entry???) was defined as the point where the cable company's cables are entering the premises of the customer's structure.

So what is the deal here then? I don't seem to get it.

I posted a picture for you to see clearly. Here you can see the new ground that we added and put it next to my condo's splitter, the old one in the background goes down into the ground and comes up in that green connection hub or whatever box that you can see on pic 2. We added the new ground because we could not determine whether the old one is connected to the power company's electrical meter underground somewhere or not.

So you think the way these cables are is normal?

Thank you so much again
 

Attachments

  • IMG_0600.jpg
    IMG_0600.jpg
    87.1 KB · Views: 2

JFletcher

Senior Member
Location
Williamsburg, VA
The demarcation point and the NID are one in the same. Where utility meets customer wiring. Can be in the pedestal, or box on the side of the house.

I would not have two ground wires to separate points from that splitter. I know it's a pita to see if the one ground goes back to your panel or service, or to a local rod then a #6 to the service, but a second ground is not the answer. It is liable to make things worse with ground loops.

If you've lost as much equipment as you say in the last 18 months, you need surge protectors on your coax. Grounding and bonding will not solve any problems with lightning strikes. If your coax eats a 500kV+ lightning strike, no amount of copper grounded or bonded to anything is going to save your equipment.

I know you want a 'it's the cable co's problem' answer, but I think everyone here is going to recommend surge suppression for your coax vs more/alternate grounding/bonding of your cable. I actually consider an isolated coax system more reliable than bonded to the service, so even if that green ground wire dies in the ground (i.e, isn't connected to squat) you're still better ahead imho.

The reason for that is if you lose a service neutral, and the coax is (properly, new code-wise) bonded to the panel, your coax acts as the neutral (because the cable co and POCO share grounds) and tends to melt, causing all sorts of other problems.

tl;dr: get surge suppresors for your coax at the equipment. What you have is a pretty clean and *apparently* code-compliant install.
 

Tomco

Member
The demarcation point and the NID are one in the same. Where utility meets customer wiring. Can be in the pedestal, or box on the side of the house.

I would not have two ground wires to separate points from that splitter. I know it's a pita to see if the one ground goes back to your panel or service, or to a local rod then a #6 to the service, but a second ground is not the answer. It is liable to make things worse with ground loops.

If you've lost as much equipment as you say in the last 18 months, you need surge protectors on your coax. Grounding and bonding will not solve any problems with lightning strikes. If your coax eats a 500kV+ lightning strike, no amount of copper grounded or bonded to anything is going to save your equipment.

I know you want a 'it's the cable co's problem' answer, but I think everyone here is going to recommend surge suppression for your coax vs more/alternate grounding/bonding of your cable. I actually consider an isolated coax system more reliable than bonded to the service, so even if that green ground wire dies in the ground (i.e, isn't connected to squat) you're still better ahead imho.

The reason for that is if you lose a service neutral, and the coax is (properly, new code-wise) bonded to the panel, your coax acts as the neutral (because the cable co and POCO share grounds) and tends to melt, causing all sorts of other problems.

tl;dr: get surge suppresors for your coax at the equipment. What you have is a pretty clean and *apparently* code-compliant install.

Thank you for your answer!

What kind of coax surge protection would you suggest? Is there any device that I would be able to install in that gray junction box for instance?

I actually do have surge protector (APC H15 Power Conditioner), and the coax is plugged into it by now. The only reason why it was not plugged in before was that the cable company suggested not to plug it in, because it could cause interference with the signal. Hell, if I only knew before that all the problems were related to it, I would not mind plugging it in at all!

Also, the power company advised that for a one-time initial installation fee ($44 or so), they can provide me some sort of surge protection (possibly their conditioner), and for a low monthly fee ($4.99 per month for up to $1,000 damage per year) they will reimburse me if something like this happens. In my situation, it is worth considering, I think. Or maybe not, who knows!

You seemed to be familiar with the place I live at. Did you live or work here before?
 

Tomco

Member
I have to tell you, those spikes were probably not that bad at all and could have been stopped by a surge protector, they were just enough to fry the HDMI ports on all my equipment. Which is, if you think about it, gives you the same results - costly repairs or new equipment.

Is this something worth considering?
 

JFletcher

Senior Member
Location
Williamsburg, VA
I would ask the cable company what they recommend and where. A suppresor like what you linked would be installed ahead of the first splitter in that box, yes. I dont have a particular product in mind (I dont deal with lightning damaged equipment often - maybe a call a year here). At the rate you are losing electronics, the cable co's offer may be your best bet. Your APC H15 is pretty high end; if that doesn't do it, I dont know what will. Yes, they can occasionally cause signal problems but if you're not experiencing any, or slow internet, leave it in place.

You may also want to call out a licensed electrician to check your service neutral as one going bad can cause voltage imbalances on your branch wiring and also fry electronics. That's because the a) current is looking for a path back to the source and can go thru your coax and b) your 120V loads like TVs are no longer operating at 120V in parallel, but at 240V in series. If you've had anything else blow out, or notice lights dimming/going brighter, then you'll want to make that call sooner than later.

Never been to your place - the pictures you provided were great! Do you happen to have one of the burned out HDMI ports?
 

Tomco

Member
I would ask the cable company what they recommend and where. A suppresor like what you linked would be installed ahead of the first splitter in that box, yes. I dont have a particular product in mind (I dont deal with lightning damaged equipment often - maybe a call a year here). At the rate you are losing electronics, the cable co's offer may be your best bet. Your APC H15 is pretty high end; if that doesn't do it, I dont know what will. Yes, they can occasionally cause signal problems but if you're not experiencing any, or slow internet, leave it in place.

You may also want to call out a licensed electrician to check your service neutral as one going bad can cause voltage imbalances on your branch wiring and also fry electronics. That's because the a) current is looking for a path back to the source and can go thru your coax and b) your 120V loads like TVs are no longer operating at 120V in parallel, but at 240V in series. If you've had anything else blow out, or notice lights dimming/going brighter, then you'll want to make that call sooner than later.

Never been to your place - the pictures you provided were great! Do you happen to have one of the burned out HDMI ports?

I am afraid that the cable company is going to be a dead end. After this, they would never say anything except that I should be fine because they meet requirements. And besides that, "Act of Nature", of course.

Ahead of the first splitter, you mean in the DP or that little box on the side of the house?

Thank you, tried my best with the pics. And yes, I actually have the dead Main Board of my TV and I also have the fried HDMI Assy for the AV receiver.
 

winnie

Senior Member
Location
Springfield, MA, USA
Occupation
Electric motor research
This being an internet forum I am surprised that you don't yet have 14 different opinions from 6 different posters

You absolutely _must_ bond the cable system shield to the electrical system ground. Code requires this, but there is actually a very good reason.

When lightning strikes, huge currents flow through the Earth. When you have two systems with _separate_ grounding electrodes, then these earth currents can flow into one grounding electrode system, through your equipment, and out the other grounding electrode system. You want these currents to stay in the grounding electrode system, passing through your bonding jumpers.

I understand the issue that JFletcher raises; the multiple neutral-ground bonds between neighbor's services can mean that an open neutral at one home can cause current flow on things like water pipes and co-ax shields. IMHO this is a real problem, but the solution is not isolated grounding electrodes.

-Jon
 

Tomco

Member
This being an internet forum I am surprised that you don't yet have 14 different opinions from 6 different posters

You absolutely _must_ bond the cable system shield to the electrical system ground. Code requires this, but there is actually a very good reason.

When lightning strikes, huge currents flow through the Earth. When you have two systems with _separate_ grounding electrodes, then these earth currents can flow into one grounding electrode system, through your equipment, and out the other grounding electrode system. You want these currents to stay in the grounding electrode system, passing through your bonding jumpers.

I understand the issue that JFletcher raises; the multiple neutral-ground bonds between neighbor's services can mean that an open neutral at one home can cause current flow on things like water pipes and co-ax shields. IMHO this is a real problem, but the solution is not isolated grounding electrodes.

-Jon

Thanks for the reply, Jon!

Are you saying that the splitter in the cable box has to be grounded and bonded back to the electrical? Because it is, that is what we did with that ground cable. Or are you talking about the ones in the box on the side of the house? Pardon my stupidity.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
For lightning protection purposes, the cable shield needs to be connected to the GES at the point of entry (demarc on side of house) and a lightning protector (spark gap or gas tube typically) needs to effectively clamp the center conductor of the coax.
You can ground the shield as many places as you want beyond that. It will typically be grounded to the EGC of the power cord of the set top box if it has one. Otherwise the cable box metal is instead grounded through the cable shield only.
 

JFletcher

Senior Member
Location
Williamsburg, VA
I am afraid that the cable company is going to be a dead end. After this, they would never say anything except that I should be fine because they meet requirements. And besides that, "Act of Nature", of course.

Ahead of the first splitter, you mean in the DP or that little box on the side of the house?

Thank you, tried my best with the pics. And yes, I actually have the dead Main Board of my TV and I also have the fried HDMI Assy for the AV receiver.

In the box in post #3, where the ground wire is. Cable co feed (single coax), then the suppresor, then the first splitter. A surge suppressor may also be an isolator, which will allow signal but no current to pass - this also will prevent a lost service neutral from using the coax as a conductor. They do have a bit of loss, so installing one on a system on the edges of its signal strength can potentially cause issues.
 

hbiss

EC, Westchester, New York NEC: 2014
Location
Hawthorne, New York NEC: 2014
Occupation
EC
Thing is you have no business in that MDU box or tampering with that wiring. MDU boxes are like electric meters, it belongs to the cable company and is supposed to be secure to prevent theft of service. I understand you have a problem, but I don't know what you yourself can do about it other than complaining to the cable company. First this is a multi-unit condo not owned by you and second, none of any of what you have showed is under your control. It's not for you or us to decide if there are problems or something doesn't meet code, it belongs to the cable company and trying to get them to change something on the say so of you or an internet forum is not going to go anywhere.

Is anyone else in the other units having similar problems?

-Hal
 

Tomco

Member
Thing is you have no business in that MDU box or tampering with that wiring. MDU boxes are like electric meters, it belongs to the cable company and is supposed to be secure to prevent theft of service. I understand you have a problem, but I don't know what you yourself can do about it other than complaining to the cable company. First this is a multi-unit condo not owned by you and second, none of any of what you have showed is under your control. It's not for you or us to decide if there are problems or something doesn't meet code, it belongs to the cable company and trying to get them to change something on the say so of you or an internet forum is not going to go anywhere.

Is anyone else in the other units having similar problems?

-Hal

Dear Hal,

I honestly do not understand your tone.

First of all, I know it is not under my control, this is the only reason why this installment is still the way it is. Second, all the pictures were taken when cable company field technician was present. He was the one who opened the box for me on my request. And yes, so far I know about four other units who lost electronics, and several others who lost cable company equipment in that time.

I will post an update really soon, with new pictures. My landlord, who lives in a different condo and lost a 65" Samsung LED TV, called the cable company and without any hassle, they installed a ground block for him in that little box on the side of the house that is now being attached to a ground rod.

The reason why I posted this is simple - if the cable company cannot decide what is right and code compliant, I might have to take control of things myself. Or at least wait for HOA to come up with a solution.
 

hbiss

EC, Westchester, New York NEC: 2014
Location
Hawthorne, New York NEC: 2014
Occupation
EC
Your beef is with the cable company. Really, your post doesn't even belong here as you are not related to the electrical industry. The last thing we need is our advice to you being used as evidence in a legal action.

-Hal
 

Tomco

Member
Your beef is with the cable company. Really, your post doesn't even belong here as you are not related to the electrical industry. The last thing we need is our advice to you being used as evidence in a legal action.

-Hal
I respect the forum rules and I am not planning on taking this to court at all, I do not know what you are talking about. Out of my 29 years, I had spent 26 in another country where people deal with their everyday problems themselves. I do not need a second income. I only want to see if there is an issue that needs to be fixed or should I just suck it up.

Here is the picture I have taken of my landlord's latest installment, that was made by the cable co. He had to deal with the same issue and for some reason, the cable co. put on a ground block for him and grounded it. So why is that?
 

Attachments

  • IMG_0705.JPG
    IMG_0705.JPG
    62.9 KB · Views: 0
  • IMG_0704.JPG
    IMG_0704.JPG
    66.7 KB · Views: 0

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
I don't see anything obviously "wrong" with the install.

I think your only real option is to install some kind of surge protection on the coax at the unit you are trying to protect.

I don't know exactly what you mean by "lost a number of equipment already" or by "I was able to successfully trace the problem back to the coaxial cables".

A lot of this kind of equipment has pretty high failure rates anyway, and you may have gotten just a bunch of bad equipment. Especially if it came from a cable company. I don't know how you could trace the failures back to the coax. just because they are all hooked to the coax does not mean the failure is there. i don't know what your level of expertise is in forsenic examination of failed electronic equipment but my guess is you are no where near knowledgeable enough to be making this kind of call.

Cable Tv boxes are notorious for having firmware issues that get worse with time. I have personally had three cable TV boxes that failed. My personal opinion is it was all firmware related. It is roughly analogous to how windows computers can get worse as software updates pile up. The latest one I got has been running fine for about 3 years now.

My suggestion - get a plug in surge protector that also has surge protection for coax and install one at each device.

I am not recommending this particular surge protector, just showing you an example of such a unit.

http://www.apc.com/shop/us/en/produ...xzr-yFWk0Uoh-jESZYuPRdl9zIeXN5UYaAkReEALw_wcB

I would also want surge protection for any ethernet cables as well.

You might also consider a ground loop isolator. This is also not a recommendation, just an example.

https://www.amazon.com/TII-220-Ground-Isolator-applications/dp/B0070Q6URO

I would be inclined to install such a device downstream of the surge protector at each unit, if I were inclined to install such a device.
 
Last edited:

Tomco

Member
I don't see anything obviously "wrong" with the install.

I think your only real option is to install some kind of surge protection on the coax at the unit you are trying to protect.

I don't know exactly what you mean by "lost a number of equipment already" or by "I was able to successfully trace the problem back to the coaxial cables".

A lot of this kind of equipment has pretty high failure rates anyway, and you may have gotten just a bunch of bad equipment. Especially if it came from a cable company. I don't know how you could trace the failures back to the coax. just because they are all hooked to the coax does not mean the failure is there. i don't know what your level of expertise is in forsenic examination of failed electronic equipment but my guess is you are no where near knowledgeable enough to be making this kind of call.

Cable Tv boxes are notorious for having firmware issues that get worse with time. I have personally had three cable TV boxes that failed. My personal opinion is it was all firmware related. It is roughly analogous to how windows computers can get worse as software updates pile up. The latest one I got has been running fine for about 3 years now.

My suggestion - get a plug in surge protector that also has surge protection for coax and install one at each device.

I am not recommending this particular surge protector, just showing you an example of such a unit.

http://www.apc.com/shop/us/en/produ...xzr-yFWk0Uoh-jESZYuPRdl9zIeXN5UYaAkReEALw_wcB

I would also want surge protection for any ethernet cables as well.

You might also consider a ground loop isolator. This is also not a recommendation, just an example.

https://www.amazon.com/TII-220-Ground-Isolator-applications/dp/B0070Q6URO

I would be inclined to install such a device downstream of the surge protector at each unit, if I were inclined to install such a device.

Thank you for your response, that ground loop isolator might be a good idea, I'll look into it!
 