Lack of Knowledge

Status
Not open for further replies.

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
I was looking at a proposed panel change from fuses to breakers. The customer has a "handyman" working there and he told me he knew all about the electrical if I had any questions. He then proceeded to tell me that he had grounded all of the non-grounded receptacles. I asked him exactly what he meant and what he did. He told me that the NM was just a 2-wire and he grounded them. I asked him what he did. He told me that he got those green pigtails for grounding and screwed them to the back of the boxes and then to the new 3-prong receptacles that he installed. I asked him if he ran a EGC (grounding conductor) to the boxes. He said no but the boxes were now grounded.:unsure:
I tried to explain to him that unless a ground wire was run to the box that it was not grounded. He then told me that a "good family friend" that was an electrician taught him to do this. I asked if maybe he missed part of the instructions about needing the ground wire from the panel or another grounded outlet. I don't think I got through to him!
I'm not even sure if the boxes are even metal as I didn't look at them.

If I get the job, I'm just going to tell the HO about the falsely grounded receptacles and let them decide what to do. I'll just change the panel and if they want me to correct this I will. Otherwise I'll just do the panel and be done with it.
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
I was looking at a proposed panel change from fuses to breakers. The customer has a "handyman" working there and he told me he knew all about the electrical if I had any questions. He then proceeded to tell me that he had grounded all of the non-grounded receptacles. I asked him exactly what he meant and what he did. He told me that the NM was just a 2-wire and he grounded them. I asked him what he did. He told me that he got those green pigtails for grounding and screwed them to the back of the boxes and then to the new 3-prong receptacles that he installed. I asked him if he ran a EGC (grounding conductor) to the boxes. He said no but the boxes were now grounded.:unsure:
I tried to explain to him that unless a ground wire was run to the box that it was not grounded. He then told me that a "good family friend" that was an electrician taught him to do this. I asked if maybe he missed part of the instructions about needing the ground wire from the panel or another grounded outlet. I don't think I got through to him!
I'm not even sure if the boxes are even metal as I didn't look at them.

If I get the job, I'm just going to tell the HO about the falsely grounded receptacles and let them decide what to do. I'll just change the panel and if they want me to correct this I will. Otherwise I'll just do the panel and be done with it.
So....
if their handyman ”fixed” everything and knew everything, why isn’t he doing the panel change?
 

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
Still would need to put it on ground fault breakers since it’s two wire, unless it was wired in ac. Have seen houses wired in ac, but not many. Apparently in the 60’s, the City of Atlanta must have required it. The only place in the south I’ve run across it. Don’t know where your at, might be common.
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
So....
if their handyman ”fixed” everything and knew everything, why isn’t he doing the panel change?
That was my first question (that I didn't ask). He sounded like he was trying to impress the HO and me, but he failed miserably with me anyway!
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
Maybe there are metal boxes fed with the newer ac cable
Still would need to put it on ground fault breakers since it’s two wire, unless it was wired in ac. Have seen houses wired in ac, but not many. Apparently in the 60’s, the City of Atlanta must have required it. The only place in the south I’ve run across it. Don’t know where your at, might be common.
No AC, I did see the NM when I took the cover off the fuse panel. Very few EGCs in there so I know most of it is ungrounded.
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
That was my first question (that I didn't ask). He sounded like he was trying to impress the HO and me, but he failed miserably with me anyway!
What’s going to be interesting is when you give your price.
what you want to bet the handyman tells HO he can do it cheaper and save them a little money..
Starting with no inspection..
 

Jon456

Senior Member
Location
Colorado
If I get the job, I'm just going to tell the HO about the falsely grounded receptacles and let them decide what to do. I'll just change the panel and if they want me to correct this I will. Otherwise I'll just do the panel and be done with it.
Personally, I'd inform the HO about the violations and hazards created by their "handyman" and insist on correcting these as part of the job. If they refuse, I would walk away: I wouldn't want the liability. Because you know that, as the licensed electrician that touched their system, you'll be the one who gets blamed/sued if someone gets injured or killed.
 