Lamp Post

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Anyone want to take a stab at this question?

A lamp post at a dwelling is fed underground with a 120 volt, 15 amp GFCI protected circuit run under a driveway. What is the permitted wiring method?

a) UF cable buried 12” deep
b) PVC conduit buried 12” deep
c) Rigid Metal Conduit buried 6” deep
d) All of the above
e) a) or b)
 
Yes, the correct answer is supposed to be e). This is from a practice test that I'm writing for a fellow electrician who is studying for a licensing exam and in answering the question I've always found parts of the table to be confusing. The interesting part of Table 300.5 is the note #4 which can trick one into thinking that for RMC a 6" burial depth could apply but it actually would not apply since one of the other conditions listed in the table (under a dwelling driveway) is within the question. I guess one could argue that the question should say 1 or 2 family dwelling (in my head it was implied) which may have led to Augie's answer.

4. Where one of the wiring method types listed in Columns 1 through 3 is used for one of the circuit types in Columns 4 and 5, the shallowest depth
of burial shall be permitted.
 
  • Like
Reactions: J2H