I have tenant space in mall setting. The electrical room from which the tenant space is fed out of is in basement.
The electrical room consists of trough with one service disconnect. Their is incoming electric utility service into trough but it is not connected. The service conductors are capped in trough not connected.
The trough and service disconnect are not grounded meaning their is no grounding electrode conductor from trough or service disconnect to grounding electrode system.
The scope of work is to extend empty conduit from the one service disconnect basement electric room into tenant space. Later tenant would file to connect electric utility service, grounding electrode conductor to GES and then ofcourse panelboard in its space.
My questions are following:
1. Is the work that they are doing right now extending conduit to the tenant space but utiltiy service conductor capped in trough and trough or service disconnect does have have grounding electrode conductor violation of the code?
2. Is their any danger one sees extending conduit when their is no GEC and electric service conductors are capped not connected in trough?
Thank you for your input.
The electrical room consists of trough with one service disconnect. Their is incoming electric utility service into trough but it is not connected. The service conductors are capped in trough not connected.
The trough and service disconnect are not grounded meaning their is no grounding electrode conductor from trough or service disconnect to grounding electrode system.
The scope of work is to extend empty conduit from the one service disconnect basement electric room into tenant space. Later tenant would file to connect electric utility service, grounding electrode conductor to GES and then ofcourse panelboard in its space.
My questions are following:
1. Is the work that they are doing right now extending conduit to the tenant space but utiltiy service conductor capped in trough and trough or service disconnect does have have grounding electrode conductor violation of the code?
2. Is their any danger one sees extending conduit when their is no GEC and electric service conductors are capped not connected in trough?
Thank you for your input.