Landscape lighting @ 120 volt
LYLE2231
Good Morning Friends, I'm trying to reference the code article that requires 120 volt landscape lighting to be GFCI protected. These fixtures will be hard wired in, not plugged into a receptacle. Any and all appreciated! Lyle :)
Ponchik
CA
Electronologist
I don't believe there is such a requirement.
There is one for swimming pool areas 680.22(B)(4), is this what you are looking for?
Ponchik
CA
Electronologist
Landscape light must be gfci protected if it is a residence and the wiring is 12" . Look at table 300.5 Col.4
I agree with that if the wiring is less than 12" but generally 120V landscape lighting do not require GFCI protection.
raider1
Logan, Utah
I agree with Dennis, the only thing that will drive the GFCI protection requirement of 120 volt landscape lighting is the burial depth of the wiring.
Chris