No, the gc only extends to the brick, it's two wire from the brick to the pc. I hadn't thought of that, I was only thinking if it from the safety standpoint. Thanks.It could provide a ground point for an internal shield that contains RF generated by the switching power supply in the brick.
Is the EGC connected to one side of the DC output that goes to the computer?
I suppose it could be used with a high series resistance to bleed off static electricity.
No, the gc only extends to the brick, it's two wire from the brick to the pc. I hadn't thought of that, I was only thinking if it from the safety standpoint. Thanks.
160608-0903
sii:
The simple experiment to perform is --- measure for continuity between the AC plug EGC pin and either of the two power supply ouput wires. If there is no continutity to either wire, then the EGC is not passed thru to the laptop internal common.
If no continuity is found to the laptop, then you need to open the power supply to see if EGC is used, It might connect to an input noise filter.
.
160608-1519 EDT
sii:
To investigate the power supply alone without opening it do the following:
1. Do not connect ourput cable to the laptop.
2. Separately measure DC resistance from power plug EGC pin to both the hot and neutral pins. I expect a high resistance, like near infinity.
3. Use a three prong adapter with external EGC wire. Connect a 1000 ohm 1/2 W resistor between the adapter green wire and either neutral or EGC of the wall outlet.
4. Plug the power supply into the adapter and the adapter into the wall outlet.
5. Measure the voltage across the 1000 ohm resistor.
If the voltage is about 5 V, then there is an internal capacitor of about 0.1 ufd between hot and the cord's EGC pin. About 0.5 V and there is an internal capacitance of about 0.01 ufd. Anything in this range would imply and internal input filter that includes the EGC circuit as part of the total filter operation.
.