large breakers

Status
Not open for further replies.

shaw0486

Senior Member
Location
baltimore
i am an apprentice and i am trying to learn about large breakers. what does frame mean such as (1600 amp frame). this is not the trip of the breaker , or is it? if someone could please help me understand.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I'll take a stab from a lay person's viewpoint.
1 part is simple maufacturing standarization. From a production/warehousing standpoint it' logical to mfg the brekers in "steps" the same as fusible switches.
The larger frame breakers are also designed to handle larger fault currrent, disapaiting the heat as required when they open.
I assume mfg desing based on ability to carry the load and handle the fault curent. The breakers also have to meet standards for NEMA and testing labs such as U.L.
The frame size is somewhat determined by the fault current the breaker must handle and then the "trip" size is selected for that frame basesd on the circuit (wire) ampacity. That ability to hande the fault current isi why you have 100 amp breakers you can hold in your hand along with ones it takes both hands to hold.
is that close breaker/engineering guys ??
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
nope. frame is basically physical size, trip is ampacity.
Your 1200 amp frame breaker could have a trip from 100 amps thru 1200.
Some "trip" sizes are factory set, some interchangable (often "plug-in" )and some adjustable.
You choose the frame mostly to fit the switchgear and for it's interrupting capacity (10,000 AIC, 22,000, 65000, etc. for example) and the trip to protect the circuit.
 

zog

Senior Member
Location
Charlotte, NC
The frame size is the continious current capabillity o fthe breaker. that rating is based on heat dissapation ability of the breaker that is affected by the size of the frame (and several other factors) hence the name.

Interuption rating (or Isc) is the max amount of current the breaker is capable of interupting at the systems voltage and with a inst or short time delay trip. T

hese ratings have nothing to do with at what current level the breaker will trip, but it can be confusing becase the INST and ST trip is on the nameplate (See pic) however if you look closely that is the interuption rating.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
shaw0486 said:
i am an apprentice and i am trying to learn about large breakers. what does frame mean such as (1600 amp frame). this is not the trip of the breaker , or is it? if someone could please help me understand.
Think of fuse sizes. Small cartridge fuses go up to 30a; large cartridges up to 60a. Small blade-type fuses go up to 100a, medium up to 200a, etc.

They do the same thing with breaker sizes. Imagine having to use a 200a-size breaker for a 20a circuit. Larger sizes need greater contact area, too.
 

zog

Senior Member
Location
Charlotte, NC
LarryFine said:
Think of fuse sizes. Small cartridge fuses go up to 30a; large cartridges up to 60a. Small blade-type fuses go up to 100a, medium up to 200a, etc.

They do the same thing with breaker sizes. Imagine having to use a 200a-size breaker for a 20a circuit. Larger sizes need greater contact area, too.

Not sure how this relates to the question any more than different size fries. The question is based on a confusion of the meaning of a rating, the same answer I posted applies to even a little 400A MCCB.
 