There is no max allowable voltage drop. We try to shoot for 2%, which is conservative. I think a lot of installers are ok going higher than that. We do almost entirely residential, so the distances are relatively short, and 2% is easy to hit. It is not too hard to calculate the additional wire cost in order get to a lower voltage drop and compare that with the additional energy the system would generate over its life. When you do the math, it is often cost effective to accept a relative high voltage drop. You have to be careful with your AC voltage drop, because this results in the inverter operating at a higher AC voltage relative to the serivce equipment, and if the building is already operating toward the high end of the acceptable utility range, the voltage drop from the inverter to the servcie could increase the inverter AC voltage beyond its operating range, causing it to shut down. This isn't a problem on the DC side of the inverter.