When determining whether this section applies, I have a 1000A utility service with a free standing combo 800A service disconnect / CT meter cabinet (24" wide) and a free standing combo 400A service disconnect / CT meter cabinet (24" wide). Each are separate enclosures.
Varied opinions from the field, but my interpretation of 110.26(C)(2) for large equipment is that the equipment needs to be 1200A or more and over 6' wide to require two exits if we can't use the exceptions.
The 800A main and 400A main are not additive making 1200A equipment (one opinion of an EC on site is that service disc sizes are additive) and since each piece of equipment is free standing, there is no equipment that is over 6' wide (opinion from the site is that it is different for service equipment and is additive).
The on site guys say this is the opinion of the inspector. This is in a big city, so one inspector doesn't get to be creative without the EOR pushing back if appropriate. I can easily push back, but looking for other experiences.
Varied opinions from the field, but my interpretation of 110.26(C)(2) for large equipment is that the equipment needs to be 1200A or more and over 6' wide to require two exits if we can't use the exceptions.
The 800A main and 400A main are not additive making 1200A equipment (one opinion of an EC on site is that service disc sizes are additive) and since each piece of equipment is free standing, there is no equipment that is over 6' wide (opinion from the site is that it is different for service equipment and is additive).
The on site guys say this is the opinion of the inspector. This is in a big city, so one inspector doesn't get to be creative without the EOR pushing back if appropriate. I can easily push back, but looking for other experiences.