hhsting
Senior Member
- Location
- Glen bunie, md, us
- Occupation
- Junior plan reviewer
Please see attached sketch. I have electrical room first floor of high rise. I have two doors however for both doors you have to climb steps down to get to electrical room. To get out climb steps down
In the electrical room I have three switchboards. All three large equipment as follows:
a. 4000A 208/120V three phase switchboard label 208/120V three phase in attached sketch
b. 4000A 208/120V three phase switchboard label 208/120V three phase in attached sketch
c. 2000A 277/480V three phase switchboard label 480/277V three phase in attached sketch
If you climb the top stairs when inside electrical room you go to loading dock room inside building and then you can go outside building from door in loading dock
If you climb the bottom stairs when inside electrical room you go to corridor which leads to loading dock room inside building then their is door which you go outside building from loading dock room
The two 208V switchboards are opposite each other with distance of 9.5 feet. The minimum distance from switchboard diagonal to top door bottom is 15 feet and 10 feet
The 480V switchboard is downstream of 208V switchboard same room. The distance from switchboard to bottom door wall is 14 feet. Distance from 480V switchboard to bottom of stairway is 10 feet.
Their is within 5 feet of 480V switchboard steel column.
All the above in attached sketch below
Questions:
1. Do the switchboards configuration comply with NEC 2017 section 110.26(C)(2)(b), or 110.26(C)(2)or not? If it does then which one? Since their are three switchboards I cannot tell
2. Egress from electrical room leads to loading room not outside. Is their a rule in any code that says egress from electrical room lead to corridor or outside for high rise?
3. Does NEC 2017 section 110.26(C)(3) mean switchboards have to be located 25 feet from door or switchboards can be located more then 25 feet away from door? Not clear
In the electrical room I have three switchboards. All three large equipment as follows:
a. 4000A 208/120V three phase switchboard label 208/120V three phase in attached sketch
b. 4000A 208/120V three phase switchboard label 208/120V three phase in attached sketch
c. 2000A 277/480V three phase switchboard label 480/277V three phase in attached sketch
If you climb the top stairs when inside electrical room you go to loading dock room inside building and then you can go outside building from door in loading dock
If you climb the bottom stairs when inside electrical room you go to corridor which leads to loading dock room inside building then their is door which you go outside building from loading dock room
The two 208V switchboards are opposite each other with distance of 9.5 feet. The minimum distance from switchboard diagonal to top door bottom is 15 feet and 10 feet
The 480V switchboard is downstream of 208V switchboard same room. The distance from switchboard to bottom door wall is 14 feet. Distance from 480V switchboard to bottom of stairway is 10 feet.
Their is within 5 feet of 480V switchboard steel column.
All the above in attached sketch below
Questions:
1. Do the switchboards configuration comply with NEC 2017 section 110.26(C)(2)(b), or 110.26(C)(2)or not? If it does then which one? Since their are three switchboards I cannot tell
2. Egress from electrical room leads to loading room not outside. Is their a rule in any code that says egress from electrical room lead to corridor or outside for high rise?
3. Does NEC 2017 section 110.26(C)(3) mean switchboards have to be located 25 feet from door or switchboards can be located more then 25 feet away from door? Not clear