Large (order of magnitude 2MVA substation and need for room

Status
Not open for further replies.

mshields

Senior Member
Location
Boston, MA
So long as the insulation rating for the transformer is above 150 degrees and in an industrial setting; in a manufacturing plant, does a 15kV to say a 2000kVA VPI transformer to 480Y/277V 1558 switchgear have to be in a room? Would OSHA have something to say about it and/or NFPA 70E?
 
I put 15kV primary, 480V secondary 2MVA liquid filled FR3 transformers in regular commercial occupancies (Group B) not in a vault.

So yes, a dry type in an industrial; occupancy does not need to be in a room.
 
I would guess that I have seen more of these units in open areas than in dedicated rooms.
 