I have a nontypical (for me) service I'm currently working on. It is a multi tenant building with two separate 4000 amp services, service #1 and service #2. Service 1 is your straight forward utility transformer --> ct cabinet --> main breaker --> distribution panels etc. type of service. Service #2 is a little different as where instead of the transformer secondary going straight to a CT cabinet and then into the building the secondary instead goes to a sectional cabinet and then into the building, no metering yet. Once in the building it goes right to a gear lineup that includes a 4000 amp breaker section buss tied to an I-line distribution section which is buss tied to a 1600 amp breaker section which then goes to a CT cabinet inside the building. The 1600 CT cabinet feeds a service rated ATS which then runs off and serves the loads designated for it. The I-line distribution section has (2) 800 amp breakers feeding (2) 800 amp meter packs for multiple commercial tenants. The gear lineup for service 2 is wired exactly as it would be if it were downstream from the utility meter, i.e. neutral/ground bond in the main section. My question is whether or not any of this wiring is under the purview of the NEC before it hits a utility's meter? In actuality "service #2" will feed multiple services and each service will be treated and wired accordingly but I'm just not used to seeing so much equipment before any actual metering. Hope this makes sense, thanks for any input.