Hello,
New to this forum. New to specifying large transformers.
Starting with the load and working backwards.
Two 600 HP, 480 VAC, 60 Hz, three phase motors. NEC FLC = 720 A. Nameplate FLA = 656 A.
Using NEC FLC for branch (single motor) conductor and breaker sizing
720 A x 1.25 = 900 A
350 kcmil at 75 C : 310 A. Three runs (separate conduits) of 350 kcmil = 930 A. OK!
838 A soft starter, good for 2933 A for 30 sec starting, set for 3.5 x 656 A = 2296 A current limited starting.
720 A x 1.75 = 1260 A. Using motor duty 1200 A three pole breaker (Siemens ND63B12).
One 7.5 KVA lighting transformer, 480 VAC, 60 Hz, single phase, 16 A full load current, 30 A two pole breaker
Feeder (combined load) conductor
900 A + 720 A + 16 A = 1636 A
300 kcmil at 75 C : 285 A. Six runs (separate conduits) of 300 kcmil = 1710 A. OK!
Feeder (combined load) breaker
1200 A + 720 A + 16 A = 1936 A
Next standard size lower = 1600 A
Since this is so far below, better use 100% motor duty breaker.
I think that I am good to here. Any comments?
For transformer sizing, I am using nameplate FLA (656 A) and estimated 8 hour average load (80%)
656 A + 656 A + 16 A = 1328 A
1328 A x 0.80 = 1062 A
1062 A x 480 V x 1.732 / 1000 = 883 KVA 8 hour average transformer load
So, 1000 KVA transformer. Do you agree?
1000 KVA Delta to Delta transformer. Secondary: 480 VAC, 60 Hz, three phase, 1204 A
Following NEC Table 450.3(A) or 450.3(B), secondary breaker 125% full load current, next size higher
1204 A x 1.25 = 1505 A : next standard size higher = 1600 A
This matches the 1600 A breaker from the feeder (combined load) determination;
and the conductors (1710 A) are good too.
Am I good to go with this set up?
Now, Question 2:
240.21(C)(3)
Less than 600 V primary with 125% fusing or breaker.
(This would be for a South Korean installation, 380 VAC, 60 Hz stepped-up to 480 VAC, 60 Hz)
Industrial installation, secondary conductors not over 25 feet, well protected.
Can I remove the 1600 A breaker and run the feeder (combined load) conductors directly to the transformer?
Now, Question 3:
Does 240.21(C)(3) apply to greater than 600 V primary with 125% fusing or breaker?
(This would be for a USA installation, 2400 VAC, 60 Hz stepped-down to 480 VAC, 60 Hz)
Industrial installation, secondary conductors not over 25 feet, well protected.
Can I remove the 1600 A breaker and run the feeder (combined load) conductors directly to the transformer?
Thank You! I greatly appreciate your input.
New to this forum. New to specifying large transformers.
Starting with the load and working backwards.
Two 600 HP, 480 VAC, 60 Hz, three phase motors. NEC FLC = 720 A. Nameplate FLA = 656 A.
Using NEC FLC for branch (single motor) conductor and breaker sizing
720 A x 1.25 = 900 A
350 kcmil at 75 C : 310 A. Three runs (separate conduits) of 350 kcmil = 930 A. OK!
838 A soft starter, good for 2933 A for 30 sec starting, set for 3.5 x 656 A = 2296 A current limited starting.
720 A x 1.75 = 1260 A. Using motor duty 1200 A three pole breaker (Siemens ND63B12).
One 7.5 KVA lighting transformer, 480 VAC, 60 Hz, single phase, 16 A full load current, 30 A two pole breaker
Feeder (combined load) conductor
900 A + 720 A + 16 A = 1636 A
300 kcmil at 75 C : 285 A. Six runs (separate conduits) of 300 kcmil = 1710 A. OK!
Feeder (combined load) breaker
1200 A + 720 A + 16 A = 1936 A
Next standard size lower = 1600 A
Since this is so far below, better use 100% motor duty breaker.
I think that I am good to here. Any comments?
For transformer sizing, I am using nameplate FLA (656 A) and estimated 8 hour average load (80%)
656 A + 656 A + 16 A = 1328 A
1328 A x 0.80 = 1062 A
1062 A x 480 V x 1.732 / 1000 = 883 KVA 8 hour average transformer load
So, 1000 KVA transformer. Do you agree?
1000 KVA Delta to Delta transformer. Secondary: 480 VAC, 60 Hz, three phase, 1204 A
Following NEC Table 450.3(A) or 450.3(B), secondary breaker 125% full load current, next size higher
1204 A x 1.25 = 1505 A : next standard size higher = 1600 A
This matches the 1600 A breaker from the feeder (combined load) determination;
and the conductors (1710 A) are good too.
Am I good to go with this set up?
Now, Question 2:
240.21(C)(3)
Less than 600 V primary with 125% fusing or breaker.
(This would be for a South Korean installation, 380 VAC, 60 Hz stepped-up to 480 VAC, 60 Hz)
Industrial installation, secondary conductors not over 25 feet, well protected.
Can I remove the 1600 A breaker and run the feeder (combined load) conductors directly to the transformer?
Now, Question 3:
Does 240.21(C)(3) apply to greater than 600 V primary with 125% fusing or breaker?
(This would be for a USA installation, 2400 VAC, 60 Hz stepped-down to 480 VAC, 60 Hz)
Industrial installation, secondary conductors not over 25 feet, well protected.
Can I remove the 1600 A breaker and run the feeder (combined load) conductors directly to the transformer?
Thank You! I greatly appreciate your input.