carter3933
Member
- Location
- North Carolina
On page 9-9 in Stallcup's study guide it says:
The motor's total full-load current rating shall be calculated at 25 or 125 percent per 220.14(C) and 220.50, which is required per 430.24 and 430.25, for calculating the load of one or more motors with other loads.
This is in reference to residential calculations - single-family dwellings.
My question is where does the "25 percent" come from and how is it applied?
I only see 125 percent in code.
Thanks,
Ron
The motor's total full-load current rating shall be calculated at 25 or 125 percent per 220.14(C) and 220.50, which is required per 430.24 and 430.25, for calculating the load of one or more motors with other loads.
This is in reference to residential calculations - single-family dwellings.
My question is where does the "25 percent" come from and how is it applied?
I only see 125 percent in code.
Thanks,
Ron