lashing of service
troyalot
what are the lashing requirements for service entrance conductors ,line side of main fusing, where they enter a 60 inch "top hat" box on top of the gear. there is about 5-6 feet of conductor from the mouth of the pipes to the main lugs. I feel they need lashing to hold them under a fault condition, but is it required and what is common practice. there are 6 parallel runs of 600kcmil. 3phase 208/120.
Re: lashing of service
has anyone built a service where the conductors needed lashing(securing). i know that typically the length is such that it is not necessary. however i have an unusual situation here. the service entrance(underground pvc) enters the basement at 12 feet above the floor and 6 feet above the lugs. so i have a factory "pull box" full of unfused service conductors hanging freely for 6 feet. any suggestions ?
314.28(B) Conductors in Pull or Junction Boxes.
In pull boxes or junction boxes having any dimension over 6 ft , all conductors shall be cabled or racked up in an approved manner.
Troy
I have seen the use of Kindorf with tywraps and rubber on the Kindorf used in the box to support the conductors, there are other means. I have also seen the use of fiberglass supports.
[ February 28, 2006, 10:21 PM: Message edited by: pierre ]
I have lashed conductors in an MCC and a CT can, both per the mfgs requirements.
The CT Can took about 200 ft of 1/2" nylon rope, sure looked nice when I was done.
For the HAT box check the instructions.
For the second question, I would ask whats the available fault current? The fault current is the basis for lashing.
This is not an Instructor topic, so it is being moved to an NEC thread. Please feel free to continue your discussion there. :)
Troyalot,
I think you just need someone to tell you to do it.
Go get some rope and start doing what you gotta do!