On a project with an Owner-furnished 400A latching/unlatching type contactor. The contactor was designed to open upon signal from the FACP to shut down fans in the building. The FACP provides a constant 120V signal for this operation and when applied, it smoked the latch coil. Looks like this contactor is designed for momentary contact push buttons, but I might be missing something? When I look at the SqD website, it says something about the latch and unlatch not being rated for constant voltage and should be wired to the "coil clearing contacts" per the instruction sheet. Cant find an instruction sheet and don't know what this might look like??
The contactor is a Square D 8903 series SY.
Ideas?
The contactor is a Square D 8903 series SY.
Ideas?