So, machine shop. There's a Carrier Infinity AC unit which has a 100% variable compressor in it with a lot of electronics. There's a couple CNC lathes in the shop. When the AC unit is trying to run at it's upper end of speed and one of the lathes completes a cycle and it's VFD brakes the spindle motor, it causes an over current fault on the AC compressor unit...
You can put an amp meter on the line going to the AC unit and it will be pulling about 8 amps at 100%, then over the course of a second or two while the lathe is stopping it will push up to 10-10.5 amps. The control in the AC unit logs an over current condition and kicks the compressor out for a few minutes before it restarts, at which time the next lathe that ends it's cycle kicks it back out again. Eventually it has enough of this and just locks out completely.
There is no way in the control to limit the compressor speed to say, 50%. It's going to do what it wants to do.
I've tried a buck transformer to drop the voltage from 245 down to about 222, but it didn't seem to make any difference at all. I can't really detect any voltage increase coming from the lathes, at least not with a DMM. I have seen where a braking VFD can push a higher frequency out onto the incoming line.
What can I put on the line going to this AC unit that would smooth out the power going to it? Power conditioner? Sine wave filter? Anybody have any recommendations?
You can put an amp meter on the line going to the AC unit and it will be pulling about 8 amps at 100%, then over the course of a second or two while the lathe is stopping it will push up to 10-10.5 amps. The control in the AC unit logs an over current condition and kicks the compressor out for a few minutes before it restarts, at which time the next lathe that ends it's cycle kicks it back out again. Eventually it has enough of this and just locks out completely.
There is no way in the control to limit the compressor speed to say, 50%. It's going to do what it wants to do.
I've tried a buck transformer to drop the voltage from 245 down to about 222, but it didn't seem to make any difference at all. I can't really detect any voltage increase coming from the lathes, at least not with a DMM. I have seen where a braking VFD can push a higher frequency out onto the incoming line.
What can I put on the line going to this AC unit that would smooth out the power going to it? Power conditioner? Sine wave filter? Anybody have any recommendations?