Laundry circuit requirements

Status
Not open for further replies.

Jose cisnero

Member
Location
Miami
Occupation
Electrician
do the Nec Requirements for laundry circuit installation or receptacles included the washing machine..?
Can I feed any convenient outlet in the laundry room and washing machine with same 20am circuit..
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Code uses the term Laundry Area and Laundry Equipment in 210.52(F) "at least one outlet shall be installed in areas designated for the installation of laundry equipment".
The laundry area could be in a bedroom...
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Can you install an individual 15 amp circuit for the washer and then have separate 20 amp convenience outlets?

I believe it is ambiguous by code wording but IMO, the nec requires a 20 amp laundry receptacle outlet. The washer is to launder so imo the 20 amp cir needs to be by the washer
 

Beaches EE

Senior Member
Location
NE Florida
Occupation
Electrical Engineer / Facilities Manager
The code minimum is 1-20A circuit for the laundry area. If a washing machine (and gas dryer) are installed AND ironing will be done in the same area, then 2-20A circuits is a better design.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Can you install an individual 15 amp circuit for the washer and then have separate 20 amp convenience outlets?
210.52(F) in discussing the laundry circuit states "for laundry equipment".. IMO, the washer would need to be on that 20 amp circuit.
 