When calculating the load for a suite in multifamily building with common laundry facilities is it necessary to include the 1500VA for a laundry circuit in the suite calculations even though there is no laundry in the suite?
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
No. But getting to that conclusion is a bit convoluted.
  • 220.52(B) says to include 1500 VA for the circuit required by 210.11(C)(1). No exceptions.
  • 210.11(C)(1) says you must include a 20 amp branch circuit to supply the laundry receptacle required by 210.52(F). No exceptions.
  • 210.52(F) says to install a laundry receptacle. But it gives two exceptions, and your case is one of the exceptions.
  • So 210.52(F) doesn't require a receptacle.
  • So 210.11(C)(1) doesn't require a branch circuit.
  • So 220.52(B) doesn't require including 1500 VA in the calculation.
  • QED
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
Glad to be of service. Now all we have to do is to wait for someone to disagree, and we can turn this into one of our famous 200+ post threads. :lol: :lol:
 